Field report - portable generator Westinghouse iGen2500
Aug 28, 2018 20:10:35 GMT
Post by rdubs on Aug 28, 2018 20:10:35 GMT
Hi everyone
I own a SO469 and make it a hobby to try and keep hours off both the motor and the built-in Cummins Onan generator. I was looking for an alternative to running the main generator at night while at anchor and thought I would try out the Westinghouse iGen2500. Many cruisers use the famous Honda EU2200i (upgraded version of the EU2000i), but I was drawn to the Westinghouse because the noise level is about the same, the power output is higher, and the cost is about half.
The big question was, can the portable generator withstand the starting surge from the air conditioning. For most generators the initial starting surge from the compressor kicking on will overload the generator, so to counteract this owners install a "soft start" system which slowly ramps the voltage up. I did not want to mess the the air conditioners, rather if a single generator wouldn't hack it then I would just buy another and run them in parallel. Also, the cost of one of the soft start devices runs about $300-$350, so a second generator would only cost about $300 more yet provide a lot more options.
To connect the generator to the shore power inlets, I bought two six foot long, 14 AWG extension cords and also two pigtail adapter cords (5-15P to L5-30R). The generator has two 115VAC plugs, so one plug went to each shore power receptacle. I sat the unit on the lowered swim platform to insulate it a bit plus get the exhaust away from the boat.
First I tested the owner's cabin AC unit, which I think is a 10K BTU one (it might be 16). For these tests I kept the battery charger off so the generator started with no load. The generator started the compressor like a champ. You could hear the RPM's dip then rev back up before becoming stable, but it held no problem. Then I tried it on the main salon 16K unit (Dometic DTU16 Turbo). The generator started this one as well. I watched the AC voltage meter on the electrical panel, it would dip to about 70 before coming back, but the important thing is it started without the generator tripping. So test successful, you don't need a soft start with this generator to get it to start your A/C unit. However, if I wanted to run a second AC, I'd need a second unit.
One note however. With the generator powering the salon AC and the compressor going, I switched on the battery charger. As the two battery chargers ramped their voltage up, the generator bogged down and eventually tripped offline. So then I turned the AC off and turned the battery charger on. You could hear the generator bog down a bit, but once the voltage stabilized it went back to normal. I then tried to start the main AC with the battery charger on, and that worked. So, lesson learned, turn the battery charger on and let the load get stabilized, and then turn the AC on.
One last item, I need to bond the ground and neutral at the generator. Like the Honda EU-series, these generators come unbound since the manufacturer doesn't know if the circuit will be bound elsewhere. My plan to bind the two is to buy a plug from Home Depot, connect a wire between the two inside the plug housing, then run a short wire to a receptacle. So create a little 6" long pigtail which binds the neutral and ground.
The specs say this generator will run for 10 hours at 25% load off the internal tank. Can't find the estimated duration at 75% load. So I'm looking into getting an extended run cap and getting that set up, that way don't have to wake up halfway through the night to refill the tank.
Sorry for the long wall of text but if anyone wants an alternative to running their built-in generator, this little guy did a great job and is a lot more affordable than the EU2200i. The EU2200i has a larger cylinder displacement (120cc vs. 100cc, if I recall), which makes it bog down less and recover better from when a surge load hits, but as I was hoping the iGen2500 can handle it.
Happy sailing
-'Dubs
I own a SO469 and make it a hobby to try and keep hours off both the motor and the built-in Cummins Onan generator. I was looking for an alternative to running the main generator at night while at anchor and thought I would try out the Westinghouse iGen2500. Many cruisers use the famous Honda EU2200i (upgraded version of the EU2000i), but I was drawn to the Westinghouse because the noise level is about the same, the power output is higher, and the cost is about half.
The big question was, can the portable generator withstand the starting surge from the air conditioning. For most generators the initial starting surge from the compressor kicking on will overload the generator, so to counteract this owners install a "soft start" system which slowly ramps the voltage up. I did not want to mess the the air conditioners, rather if a single generator wouldn't hack it then I would just buy another and run them in parallel. Also, the cost of one of the soft start devices runs about $300-$350, so a second generator would only cost about $300 more yet provide a lot more options.
To connect the generator to the shore power inlets, I bought two six foot long, 14 AWG extension cords and also two pigtail adapter cords (5-15P to L5-30R). The generator has two 115VAC plugs, so one plug went to each shore power receptacle. I sat the unit on the lowered swim platform to insulate it a bit plus get the exhaust away from the boat.
First I tested the owner's cabin AC unit, which I think is a 10K BTU one (it might be 16). For these tests I kept the battery charger off so the generator started with no load. The generator started the compressor like a champ. You could hear the RPM's dip then rev back up before becoming stable, but it held no problem. Then I tried it on the main salon 16K unit (Dometic DTU16 Turbo). The generator started this one as well. I watched the AC voltage meter on the electrical panel, it would dip to about 70 before coming back, but the important thing is it started without the generator tripping. So test successful, you don't need a soft start with this generator to get it to start your A/C unit. However, if I wanted to run a second AC, I'd need a second unit.
One note however. With the generator powering the salon AC and the compressor going, I switched on the battery charger. As the two battery chargers ramped their voltage up, the generator bogged down and eventually tripped offline. So then I turned the AC off and turned the battery charger on. You could hear the generator bog down a bit, but once the voltage stabilized it went back to normal. I then tried to start the main AC with the battery charger on, and that worked. So, lesson learned, turn the battery charger on and let the load get stabilized, and then turn the AC on.
One last item, I need to bond the ground and neutral at the generator. Like the Honda EU-series, these generators come unbound since the manufacturer doesn't know if the circuit will be bound elsewhere. My plan to bind the two is to buy a plug from Home Depot, connect a wire between the two inside the plug housing, then run a short wire to a receptacle. So create a little 6" long pigtail which binds the neutral and ground.
The specs say this generator will run for 10 hours at 25% load off the internal tank. Can't find the estimated duration at 75% load. So I'm looking into getting an extended run cap and getting that set up, that way don't have to wake up halfway through the night to refill the tank.
Sorry for the long wall of text but if anyone wants an alternative to running their built-in generator, this little guy did a great job and is a lot more affordable than the EU2200i. The EU2200i has a larger cylinder displacement (120cc vs. 100cc, if I recall), which makes it bog down less and recover better from when a surge load hits, but as I was hoping the iGen2500 can handle it.
Happy sailing